Chased a tube leak on a 300 HP boiler for 11 hours and it was a pinhole under the insulation
Had a nagging pressure drop on a packaged boiler at a school in Dayton and figured it was a bad gauge, so I swapped it out first thing Monday and lost an hour. Then I checked the feedwater valve, the traps, and pulled the burner twice thinking it was running lean. Eleven hours in, I finally cut back a 2 foot section of insulation on the rear tube sheet and there it was, a pinhole the size of a pin head spraying just enough to drop 4 psi a day. Would have caught it in 10 minutes with a moisture meter and a flashlight instead of chasing everything else. Got the tube plugged and the old girl held 150 psi all weekend. What's your go-to move for finding a leak you can't see, smoke test or just start pulling covers?