Rant: I skipped the bonding jumper on a pool pump and it came back on me 3 months later
Last summer I wired a pool pump in Sacramento and had to choose between running a separate bonding conductor back to the panel (about 60 feet of #8) or just tying into the existing grid near the equipment pad. I picked the short cut into the grid because it looked fine and passed my continuity check at the time. Three months later the homeowner called me about a tingling feeling when touching the handrail, and my tester showed 4 volts between the rail and the deck. Turns out the grid connection had corroded under the lug and the pump was energizing the water. Spent a whole Saturday redoing it with a proper #8 run and a new bronze clamp, and I'll never skip that again. Anybody else had a bonding call go sideways like that?
4 volts on a handrail is low enough that most people wouldn't even feel it, and a lug can corrode on any connection no matter how you ran it. Sounds more like a bad clamp than proof the short cut was doomed.